Can I Remove Bonding Clamp?

Somewhat of a mystery among most customers, whilst I think many of you will have probably seen what you might term an ‘earth bonding clamp’ (it’s not ‘earth bonding’, earthing & bonding are 2 separate things)

I feel sure it’s use and the importance of what it does is probably lost on you.

Have you ever asked, Can I Remove Bonding Clamp?

Whilst I won’t go into too much depth about the whole earthing / bonding debate here, if you would like to clear some of the smoke & mirrors surrounding this, please visit the appropriate page HERE

As for the humble clamp around your pipe: What is the significance of it, and why does it have a thin metallic ‘label’?

The clamp (technically known as a BS951 clamp) is designed to provide a tight, low resistance joint to metallic pipework for the purpose of providing a bonding connection.

The ‘wrap-around’ style of the clamp allows it be be applied tightly so that there is no movement, and it is also more likely to resist slight expansion forces of the pipes when heated.

The thin (often sharp!) edge on the ‘label’ has cut many a finger in the back of a kitchen cupboard! But what is the label for? Can I remove it?

The label contains a set phrase “SAFETY ELECTRICAL CONNECTION DO NOT REMOVE” and is designed to highlight the importance of the connection to end users or others who may want to tamper with it.  The label should not be removed, it would be highlighted as a C3 – IMPROVEMENT RECOMMENDED on an EICR if the label was not present.

The clamps come in a range of sizes and variations for both indoor & outdoor use:

  • E14 clamps are for internal use only and are usually red.
  • E15 clamps are for internal or external use and are usually blue.
  • E16 clamps are for internal or external use and are usually green. They also allow larger conductor sizes to be fitted (16mm or sometimes greater)

So: Can I remove bonding clamp?

Can I Remove Bonding Clamp?
Difficult to answer properly as it depends on the type of bonding to which it is pertaining and a whole host of other technical variables. To simplify things, the answer is NO, do not remove your bonding clamps. Doing so could be disconnecting a very important safety element of your electrical installation. If you do need to temporarily remove the bonding clamps whilst renovation works are taking place, these MUST be reconnected upon completion of the works.

All too often, we see DIYers, or even other trades like Plumbers, come along and remove the bonding clamps without knowing the implications of not having them installed. This is a common problem at kitchen/bathroom refits where the original connections may have been disturbed.

So if you ever ask yourself again: Can I Remove Bonding Clamp? You will know where you stand!

How not to use:

We’ve seen BS951 clamps used for a couple of purposes that they are not designed for/serve no use:

  • Bonding clamps are not designed to be used for earthing the outer armouring of SWA cables.  This should be done with the correct SWA gland as detailed HERE.  Not only is the clamp not designed for this job, cutting the sheath of the cable to allow the clamp to be fitted will allow moisture ingress into the armour wires and potentially corrode them.
  • BS951 clamps on plastic pipework.  Obviously more of an issue with newer properties, but common sense dictates that it is not going to serve much use on a section of plastic!

NOTE:  BS951 (or similar) clamps are sometimes used by the DNO (Distribution Network Owner) to provide an earth to premises.  Although this practise would not be acceptable on cables within the premises, the supply cable comes under a different set of regulations (Electricity Safety, Quality and Continuity Regulations). As such this does not apply to any main supply cables

Need anymore specific advice about the bonding in your premises? Feel free to contact me and I will be only too happy to assist

James
ElectricBlu Contractors
www.electricblu.co.uk

Defibrillator Installation Wakefield

28th December 2022
Defibrillator Installation Wakefield CALL (01924) 654034Staffed Landline During Office Hours REQUEST QUOTE ONLINERapid Response…

Do Landlords Need Metal Consumer Units?

11th August 2020
Do Landlords Need Metal Consumer Units? LATEST UPDATE Jan 2024 Introduction to Changes for Landlord Electrical Regulations There…

Boiler Electrical Installations in Wakefield – Smart Controls

11th August 2020
Boiler Electrical Installations in Wakefield LATEST UPDATE April 2022 If you are having work completed to your boiler then you should…

Share this article

Leave a comment

Your email address will not be published. Required fields are marked *